Coarse filter problem report.
We have 2 coarse filters (filter 1 and filter 2). Each filter contains a basket. They are used in the water injection system for filtering particles of more than 75u. The normal operational mode is one filter on duty and one on standby.
day 1: As normal operation, we opened filter 2 for inspection and found the basket filter had burst. This was replaced with a new basket. Filter No2 was then put on line and worked satisfactorily. No1 filter then cleaned. day 2: No1 filter again put on line as No2 filter was indicating an high DP. day 3: Filter 2 put online, and isolated filter No1, due to basket burst after backwash sequence failed to cause high DP across filter. day 4: No1 again put online, but this time without a basket. Isolated filter 2 due to an high DP again. Even manually started backwash motor for running continuously. day 5: We decided to insert yet another new basket for filter No2, and took out the existing filter for chemical cleaning.
After this step, filter No2 is online with another new basket, and can handle normal water flow through filter, and backwash sequence in auto mode as normal, but DP across filter causing an high alarm within 4 minutes of backwash being stopped.
day 6: We decided to install a new basket, which had been chemically cleaned, into filter No1. Then we put both filters online in parallel for sharing water flow through both flters. With both filters online, DP indicates an in-range figure, with backwash sequence in auto.
We have continued to monitor. _________________ Keep it simple. Keep it interesting. |
|